combining service for strip mall units

Status
Not open for further replies.

gator07

Member
Location
florida
hello guys! I just recently passed my masters exam, but i do not conduct my own business yet, i just wanted to have it in case i wanted to do small jobs or service work on side. Most of my experience is residential. I've been asked to help a friend with a small job , they have combined two units of a strip mall and there is a 2 gang meter bank whick feeds two 100 amp panels. I was thinking abount putting a 200 amp meter main combo panel in place of the meter bank and then feeding each panel with a 4 wire feeder and seperating n-g connections in each. I not sure what the best and cheapest way to do this is, any advise would be appreciated. Thanks in advance!
 

iwire

Moderator
Staff member
Location
Massachusetts
Or you could leave it as it is and they pay for two meters.

That is how we deal with it a lot around here, I have combined three units into one and they had three meters for that space.
 