marcmm
Member
- Location
- Los Angeles
110.12(A) Unused Openings. Unused openings, other than those intended for the operation of equipment, those intended for mounting purposes, or those permitted as part of the design for listed equipment, shall be closed to afford protection substantially equivalent to the wall of the equipment. Where metallic plugs or plates are used with nonmetallic enclosures, they shall be recessed at least 6 mm (1⁄4 in.)from the outer surface of the enclosure.
Bold helps... thanks so much y'all.IMO 110.12(A) applies.
Is that the outside wall of a cabinet or just a partition between sections within the cabinet? 110.12(A) wouldn't necessarily apply to such a partition.Bold helps... thanks so much y'all.
That is what I thought. I also don't feel there is much threat of this starting on fire. Heat will be a bigger issue at terminations on this kind of thing. If it started fire anyway - is likely contained to the cabinet, not enough fuel there to be sustained all that long.Looks like the divider between the utility & distribution section of a all in one panel.
Yes, its an outside wall.Is that the outside wall of a cabinet or just a partition between sections within the cabinet? 110.12(A) wouldn't necessarily apply to such a partition.
That is what I thought. I also don't feel there is much threat of this starting on fire. Heat will be a bigger issue at terminations on this kind of thing. If it started fire anyway - is likely contained to the cabinet, not enough fuel there to be sustained all that long.
shall be closed to afford protection substantially equivalent to the wall of the equipment
Yes, its an outside wall.
COULD be that the actual hole behind that plywood is a regular round conduit KO and at one time there WAS conduit for those conductors. But someone came along later and decided the conduit was unnecessary(!) then had to gin up a way to not cut the conductor insulation, so having only plywood and a table saw, came up with this DIY hack but because it was a table saw, it came out as a rectagle.So the even bigger question is why are open conductors entering the panel?
And what was the big square hole for?
-Hal
Much appreciated.COULD be that the actual hole behind that plywood is a regular round conduit KO and at one time there WAS conduit for those conductors. But someone came along later and decided the conduit was unnecessary(!) then had to gin up a way to not cut the conductor insulation, so having only plywood and a table saw, came up with this DIY hack but because it was a table saw, it came out as a rectagle.
Regardless, not kosher, no inspector in his right mind would allow it, and you will ALSO have to deal with those conductors NOT being sheathed NM/SE, so would need a raceway of some sort and a proper fitting for entering that box.
As to "combustible", that's actually not the issue here. You can use plywood for back panels in enclosures, it's done all the time. It's just not a good idea...
ditto. If there is a neutral for that circuit it should have been run through same spot when it leaves the panel, EGC also.So the even bigger question is why are open conductors entering the panel?
And what was the big square hole for?
-Hal