COMcheck Help

Status
Not open for further replies.

kenaslan

Senior Member
Location
Billings MT
I am doing a renovation of a hotel. The front lobby, dining, office, and kitchen areas will have a mixture of old and new light fixtures. Some OLD F40T12 and a few new T8s. Must I include ALL lighting in the COMcheck? Both old and new, of only the areas being refurbished? Or the entire building
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Depends on the percentage of fixtures being replaced. If you choose "Alterations" as the project type, it will ask under the lighting inputs exemptions "Less than 50% of fixtures replaced AND wattage not increased."

If you don't meet the exemption, you have to put in all the fixtures.
 