They don't need a receptacle, but if one is installed, does it need a designated 20 amp circuit?
Thank you :smile:No, there is no NEC requirement that a receptacle installed in a non-dwelling unit bathroom be on a 20 amp circuit.
Chris
No, there is no NEC requirement that a receptacle installed in a non-dwelling unit bathroom be on a 20 amp circuit.
Chris
Are receptacles even required in commercial bathrooms? I don't think they are but want to make sure. Thanks.
No they are not required but if you install one they must be GFCI protected