Do I need to use a weather resistant entry method (RT EMT conn, myers hub...) to enter the side of a 3R wireway? Dont see this spelled out anywhere.
Do I need to use a weather resistant entry method (RT EMT conn, myers hub...) to enter the side of a 3R wireway? Dont see this spelled out anywhere.
Is this a panel or just a trough or box?
Just a pull box
Agree. The general rule is raceway and cable terminations must maintain (or exceed) the degree of protection provided by the enclosure type.IMO the entry needs to be rated for wet locations.
Need to verify, but I believe you can enter with non raintight fittings below live parts or something of that nature. I say this because you do find 3R cabinets and other enclosures with factory KO's that are not all that water tight at the lower end of side walls and in the bottom wall of the enclosures.
312.2 Damp and Wet Locations. In damp or wet locations,surface-type enclosures within the scope of this articleshall be placed or equipped so as to prevent moistureor water from entering and accumulating within the cabinetor cutout box, and shall be mounted so there is at least6-mm (1⁄4-in.) airspace between the enclosure and the wallor other supporting surface. Enclosures installed in wet locationsshall be weatherproof. For enclosures in wet locations,raceways or cables entering above the level of uninsulatedlive parts shall use fittings listed for wet locations.
If the enclosure is in a wet location, how is the raceway not?It seems like a grey area to me. As mentioned, we can come into a cabinet or meter enclosure on the side without weather resistant fittings.
If the enclosure is in a wet location, how is the raceway not?
That would apply to equipment listed in Article 312 not pull boxes.
312.2 Damp and Wet Locations. In damp or wet locations,surface-type enclosures within the scope of this articleshall be placed or equipped so as to prevent moistureor water from entering and accumulating within the cabinetor cutout box, and shall be mounted so there is at least6-mm (1⁄4-in.) airspace between the enclosure and the wallor other supporting surface. Enclosures installed in wet locationsshall be weatherproof. For enclosures in wet locations,raceways or cables entering above the level of uninsulatedlive parts shall use fittings listed for wet locations.
Well that's an interesting point I hadn't considered. So you are saying that even if the wireway doesn't need a,wet location fitting, the raceway still does?
The bottom is a bit different than the side... is it not? :happyyes:Many will say you can't use a set screw connector in a bottom wall of an outdoor cabinet even if you used rain tight fittings on the rest of the run. Logic tells me it won't let any more or less water in the raceway then a rain tight fitting will at that location.
At least on sides exposed to water (penetration). That's why I earlier said...Well that's an interesting point I hadn't considered. So you are saying that even if the wireway doesn't need a,wet location fitting, the raceway still does?
... The general rule is raceway and cable terminations must maintain (or exceed) the degree of protection provided by the enclosure type.
Absolutely, you used to be able to run flexible metal conduit out the bottom in outdoor applications, I never did - but it made sense that it was allowed.The bottom is a bit different than the side... is it not? :happyyes:
I agree. I'm not sure what the deal is with all this wx resistant stuff when the conductors are rated for wet and there are other codes requiring raceways to drain, etc... but I also want to pass inspectionThere is so much unnecessary hand wringing around outdoor electrical installs I've given up on any hope of fact based rules.
Absolutely, you used to be able to run flexible metal conduit out the bottom in outdoor applications, I never did - but it made sense that it was allowed.
312.2 Damp and Wet Locations. In damp or wet locations,surface-type enclosures within the scope of this article shall be placed or equipped so as to prevent moisture or water from entering and accumulating within the cabinet or cutout box, and shall be mounted so there is at least6-mm (1⁄4-in.) airspace between the enclosure and the wall or other supporting surface. Enclosures installed in wet locations shall be weatherproof. For enclosures in wet locations,raceways or cables entering above the level of uninsulated live parts shall use fittings listed for wet locations.
Quoted by Infinity,
312.2 Damp and Wet Locations. In damp or wet locations,surface-type enclosures within the scope of this article shall be placed or equipped so as to prevent moisture or water from entering and accumulating within the cabinet or cutout box, and shall be mounted so there is at least6-mm (1⁄4-in.) airspace between the enclosure and the wall or other supporting surface. Enclosures installed in wet locations shall be weatherproof. For enclosures in wet locations,raceways or cables entering above the level of uninsulated live parts shall use fittings listed for wet locations.
IMO, you can argue that your entry into the side of the enclosure is not "Above" the uninsulated live parts. So a weatherproof entry (hub) is not necessary.
Even though it makes sense to put one on. But the code is not about making sense.
I. Scope and Installation312.1 Scope. This article covers the installation and con-
struction specifications of cabinets, cutout boxes, and meter
socket enclosures.