L lakee911 Senior Member Location Columbus, OH Oct 25, 2017 #21 Does any of this apply if the wet rated (3R, 4, 4X, 6, 6P) enclosure is installed in a dry location? Any requirement to maintain the rating?
Does any of this apply if the wet rated (3R, 4, 4X, 6, 6P) enclosure is installed in a dry location? Any requirement to maintain the rating?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Oct 25, 2017 #22 lakee911 said: Does any of this apply if the wet rated (3R, 4, 4X, 6, 6P) enclosure is installed in a dry location? Any requirement to maintain the rating? Click to expand... No NEC requirement at all to "maintain" the rating of the enclosure. You can exceed the minimum required for a particular location is you so desire.
lakee911 said: Does any of this apply if the wet rated (3R, 4, 4X, 6, 6P) enclosure is installed in a dry location? Any requirement to maintain the rating? Click to expand... No NEC requirement at all to "maintain" the rating of the enclosure. You can exceed the minimum required for a particular location is you so desire.