coming into top of 3R wireway outside

Status
Not open for further replies.

firebird1988

Member
Location
Arkansas
Occupation
Solar
So, Working on a client project. I have a wire trough outside. A Double Throw Safety Switch will be installed above with a outdoor rated breaker panel. Part number DT223URH-NP on the double throw safety switch.
The wire through will have zero splices or lived components. my understanding is that I need rain tight fittings and was going use Myers hub.
Sigma ProConnex™ 2" Rigid Insulated Raintight Hub
Model Number: 02-54075.

Now am I wasting clients' money trying to make it waterproof even tho there is zero splices or lived components inside this wire trough? Now on the backside of the wire trough will entry into the house which will have live components with same level of the wire trough but that pipe will be sealed with duck putty.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
And there can be issues with water from condensation inside. Seal all conduit runs into though,
What type of wireway/trough are you using?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
IMO your plan of using Myers hubs is fine. You could also use sealing locknuts with rigid nipples.
 
Interestingly, there doesn't seem to be a specific code requirement to use a "weatherproof" conduit entry on the top of a 3R wireway. 376.10(3) says permitted In wet locations where wireways are listed for the
purpose. Do the instructions dictate entry methods? I have never thought to look.
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
Treat the outside like no rain will get in, and the inside like it will.
Using a wire way which is a raceway. 376.22
225. 22 applies. raceways arranged to drain. Usually there is a couple holes in the bottom corner or the 3r metal wire way.
In Artical 100:
Location wet
Raintight.
Very well said Larry. 👏👏
If you don't mind I'm going to use that one at work. You will get the credit.
 

jap

Senior Member
Occupation
Electrician
Treat the outside like no rain will get in, and the inside like it will.

Ok, I'm slower than most.

Can you expand on this?

Treat the outside of the gutter like no rain will get in, and the inside of it like it will?

JAP>
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Ok, I'm slower than most.

Can you expand on this?

Treat the outside of the gutter like no rain will get in, and the inside of it like it will?
In other words, do what you can and should to prevent rain entry, but do what is necessary to allow the inevitable leakage to escape, all the while keeping energized components above any non-sealed holes.
 

jap

Senior Member
Occupation
Electrician
In other words, do what you can and should to prevent rain entry, but do what is necessary to allow the inevitable leakage to escape, all the while keeping energized components above any non-sealed holes.

So actually, "Treat the outside like rain will get in and treat the inside like it will also". :)

JAP>
 

jap

Senior Member
Occupation
Electrician
I think he means "Take steps on the outside to keep rain out, but take steps on the inside to handle rain getting in."

Cheers, Wayne

Yep, it just a fun play on words.

If you have rain getting in you didn't do a very good job of taking steps to keep the rain out. :)

Maybe, "Take steps on the outside to keep the water out, but take steps on the inside to handle any water that may have gotten in." :)

JAP>
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
A difference between compression and rain tight compression could be one example.

Out side install:
2" EMT into a hub or using a sealing locknut on top of the 3R metal wire way using compression versus rain tight compression.

2" EMT entering the bottom of the wire way.
 

jap

Senior Member
Occupation
Electrician
A difference between compression and rain tight compression could be one example.

Out side install:
2" EMT into a hub or using a sealing locknut on top of the 3R metal wire way using compression versus rain tight compression.

2" EMT entering the bottom of the wire way.
I know we all do it but not sure the threads on an EMT connector is made to be screwed into a hub.

Jap>
 
A difference between compression and rain tight compression could be one example.

Out side install:
2" EMT into a hub or using a sealing locknut on top of the 3R metal wire way using compression versus rain tight compression.

2" EMT entering the bottom of the wire way.
Tulsa, I dont quite follow. Regular compression EMT connector would not compliant outside no matter how you dress it up with a hub or sealing locknut (both of which are technically not compliant to use on a EMT connector). Why not just use a RT EMT connector right into the top by itself?
 