No, that is not possible in this case. The rating of 2/0 in the 75?C column is 175 amps and that is a standard OCPD size so there is no next larger standard size. 240.6However, if the connected load does not exceed the rating of the conductor it could be installed with the next higher breaker size. 240.4
barbeer said:Your assumptions are more than likely correct, 310.16 does not rate 2/0 CU for 200 amps in the 75 degree column which is mostly used today. However, if the connected load does not exceed the rating of the conductor it could be installed with the next higher breaker size. 240.4
It is break time here:smile:Don is supposed to be at work and not sitting here reading and responding to forum discussions at this time of day
don_resqcapt19 said:barbeer,
No, that is not possible in this case. The rating of 2/0 in the 75?C column is 175 amps and that is a standard OCPD size so there is no next larger standard size. 240.6
Don
don_resqcapt19 said:It is break time here:smile: