COMMENT 18-99 600.6(A)(1)

Status
Not open for further replies.

fmtjfw

Senior Member
I'm looking for constructive criticism on the following, and if you think it is merited, support in the form of comments from you on 18-99. Thanks, Jim Williams

4 Comment:

600.6 Disconnects.
(A) Location.
(1) At Point of Entry to a Sign Enclosure.
The disconnect shall be located at the point the feeder circuit or branch circuit(s) supplying a sign or outline lighting system shall enter the disconnect and shall not enters a sign enclosure. and shall disconnect all wiring where it The disconnect shall open all ungrounded conductors before they enters the enclosure of the sign. [ROP 18?99]

Exception: A disconnect is not required for branch or feeder circuits passing through the sign where enclosed in a Chapter 3 listed raceway. [ROP 18?99]


5 Statement of Problem and Substantiation.

The above text is clearer and, I believe, matches the admirable intent of the original proposal. Note that the exception allows the feed to pass through the sign ONLY if it is completely enclosed in a raceway.
 