I'm looking for constructive criticism on the following, and if you think it is merited, support in the form of comments from you on 8-120a. Thanks, Jim Williams
4 Comment:
revise the text as follows:
red indicates deleted text.
Green indicated duplicated text.
374.11 Connection to Cabinets and Extensions from Cells. Connections between raceways and distribution centers and wall outlets shall be made by means of liquidtight flexible metal conduit, flexible metal conduit where not installed in concrete, rigid metal conduit, intermediate metal conduit, electrical metallic tubing, or approved fittings. Where there are provisions for the termination of an
equipment grounding conductor, rigid polyvinyl chloride conduit, reinforced thermosetting resin conduit, electrical nonmetallic tubing, or liquidtight flexible nonmetallic conduit shall be permitted. Where installed in concrete, liquidtight flexible metal conduit and liquidtight flexible nonmetallic conduit shall be listed and marked for direct burial.
Informational Note: Liquidtight flexible metal conduit and liquidtight flexible nonmetallic conduit that is suitable for installation in concrete is listed and marked for direct burial.
5 Statement of Problem and Substantiation.
The informational note now just repeats the meaning of the last sentence of 374.11. It serves no purpose.
4 Comment: