Commercial: 15 amp lighting circuits ok ?

Status
Not open for further replies.

Stevenfyeager

Senior Member
Location
United States, Indiana
Occupation
electrical contractor
Is it ok to run 15 amp lighting circuits in offices? With all troffers LED now, it is easier. I only ask because I ran 15 amp outlets in a dining room in a house recently and ran into trouble, not realizing I had gone against NEC code. Thanks!
 
Is it ok to run 15 amp lighting circuits in offices? With all troffers LED now, it is easier. I only ask because I ran 15 amp outlets in a dining room in a house recently and ran into trouble, not realizing I had gone against NEC code. Thanks!
No restriction, I do it all the time. Many of these disposable led troffers have annoyingly small j boxes making 14 a good choice.
 
You ran into trouble in the house as the NEC requires 20a SABCs in the dining room.

Unless there's a local amendment or owner requirement, 15a lighting circuits are perfectly legal.
 