Commercial Bathroom Requirements

Status
Not open for further replies.

LEO2854

Esteemed Member
Location
Ma
C'mon, Dennis.... how are we supposed to stretch this thread out to 150 posts if you answer the OP on the second one? :D

I thought you wanted to strech this thread to 150 post C'mon 480 sparky:grin: you must be slacking off:D
 
I think there is a proposal to require that all commercial bathrooms use RMC and THWN for all wiring. (that oughta keep this going)

Exception No. 210.8 (G) 44....A new provision was added at 210.8(G)(44) to require GFCI protection for all 125-volt, single-phase, 15- and 20-ampere receptacles installed in commercial/Industrial bathrooms/restrooms be supplied by Extra Heavy Duty (Read Schedule 80) PVC conduit encased in knot less than 12" of concrete in walls and 24" of red concrete where fed through floors! Where fed from the keyless outlet on the ceiling... 18/2 lamp, vacuum cleaner cord or type SJOW shall be permissible!
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Exception No. 210.8 (G) 44....A new provision was added at 210.8(G)(44) to require GFCI protection for all 125-volt, single-phase, 15- and 20-ampere receptacles installed in commercial/Industrial bathrooms/restrooms be supplied by Extra Heavy Duty (Read Schedule 80) PVC conduit encased in knot less than 12" of concrete in walls and 24" of red concrete where fed through floors! Where fed from the keyless outlet on the ceiling... 18/2 lamp, vacuum cleaner cord or type SJOW shall be permissible!
"All righty, then!"
 
Exception No. 210.8 (G) 44....A new provision was added at 210.8(G)(44) to require GFCI protection for all 125-volt, single-phase, 15- and 20-ampere receptacles installed in commercial/Industrial bathrooms/restrooms be supplied by Extra Heavy Duty (Read Schedule 80) PVC conduit encased in knot less than 12" of concrete in walls and 24" of red concrete where fed through floors! Where fed from the keyless outlet on the ceiling... 18/2 lamp, vacuum cleaner cord or type SJOW shall be permissible!

Who purposed that, and why?
 