Commercial bldg

Status
Not open for further replies.

Rlmwireman

Member
Location
Evart, MI
Occupation
Electrician
I have a outdoor 5 multi meter pedestal
That will feed 4 200 amp panels and 1
100 amp panels. These are bare tenant spaces with virtually no loads other than
Minimum code requirements. How do
I figure out feeder wire size to 5 meter
Pedestal.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
I got bit in the rear by this last year, inspector required it to be sized to the breaker(s).
So ask your AHJ
 