Re: Commercial Branch Lighting Circuits
Todd,
The 80% derating factor is for a load's LCL - which would be for loads running 3 Hours or more (180 Minutes or more), AKA Continuous Loads.
If not Continuous Loads, the circuit can be run at 100% capacity. This is what I was getting at with the inclusion of the 60 Fixtures running for 179 Minutes, then turned off.
It was merely an example and FYI statement.
The 15 Amp Circuit Breaker will not trip if loaded past 12 Amps (unless it sucks!). If this was the case, they would be identified as 12 Amp Trips, instead of 15 Amp Trips.
Even if the 15 Amp breaker was to carry 100% rated current (15 Amps) for 3+ Hours, it would not trip (once again, unless it sucks!). This is where designing maximum current limits of circuits comes in.
As to loading a circuit up to 100% and running it for anything more than a few minutes, I would not do that either. I just posted that example as an FYI example.
As to LCL and Lighting circuits, for any projects I do Electrical Design/Engineering on, Lighting Circuits are figured to be LCL (Volt-Amps listed in Panel Schedules are 125% of actual connected VA) and the circuits are not loaded above 50% Capacity.
My projects are Commercial based (nearly all are Bank Branches or some type of Fin. Assoc. Clients), and involved in both Designing/Engineering of projects, plus the physical Installations (Power and Lighting, Comm/Data, CCTV/Security designs and installs).
Scott35