Not.Do apply -or not- Table 220.44 when the calculation of the receptacle load in Banks and Offices are made thru 1VA/sq ft ?
-220.14(I), is about 'load' and 220.44 established: "Receptacles loads calculated in accordance with 220.14 H and I shall be permitted to be made subject to the 'demand' factors given in Table 220.42 or 44."
-For me the 220.44 apply, but authors on 'Code calculation' differ on Table 220.44 application. I will teach this week about this calculation and I am not fully sure which one is the correct interpretation of Code.