Went on a service call today for a melted plug and recep. Got there and breaker was obviously tripped. Recep was melted good and plug even worse. Put the meter on the recep and still had power on one leg. Strange I thought, so I checked the breaker and it was leaking 70 volts through, so I changed breaker out. Now it was a 3 pole 60A breaker feeding a 60A 3 phase 4W Recep for a deep fryer. I looked at the nameplate on the fryer and it said it pulled 57amps per phase. This kinda of load on a 60A breaker violates 210.23(A)(1). I wondered why it was done this way. Does 422.11(F)(1) come into play here at all?? Could this have been hard wired and been legal as far as disconnecting means goes? The unit does have an off position. Oh by the way I swapped out the plug and recep for new ones.