dm9289
Industrial Maintenance Electrician
- Location
- Pennsylvania
- Occupation
- Industrial process repair/ maintenance Electrician
There is a 1 story block building garage that does change motors with no pits that needs a service change.
I figured this is a "major repair garage" based on the above.
From 511.3(C) it seems to me that this location is Class 1 Division 2 Zone 2 do you agree?????
Now for the Panel if im in the right place 501.115B seems to say I will need a class Class 1 enclosure or in my terms explosion proof?
Your help would be greatly appreciated
I figured this is a "major repair garage" based on the above.
From 511.3(C) it seems to me that this location is Class 1 Division 2 Zone 2 do you agree?????
Now for the Panel if im in the right place 501.115B seems to say I will need a class Class 1 enclosure or in my terms explosion proof?
Your help would be greatly appreciated