harley1959
Member
- Location
- Michigan
I have a situation where a particular location has been determined to operate as a 'commercial garage'. Within this 'commercial garage is a 'anechoic test chamber' which will be used for testing automobiles. The automobiles will be 'running' periodically during these sound tests within the chamber. The chamber is properly exhausted and vented. There are 25 air changes per hour within this chamber. Outside the chamber is a work area for the automobiles. The work area is deemed the 'commercial garage' since there will be service on these vehicles. There is 6 air changes per hour in the garage area. Problem: When fire alarm system is activated, the air handling system shuts down. I am being asked to provide interlock devices to shut down test equipment within the chamber and commercial garage areas when the fire alarm system is activated due to the fact that when the alarm is active, the air changes per hour in both the test chamber and garage area are not valid, due to their shut down, causing non hazardous type equipment, such as lighting installed 18" of the ceiling, to be required class 1, div 2 type lighting fixtures. Should electrical wiring installed within properly vented classified locations be maintained by interlock methods to shut down electrical equipment during fire alarm activation?