I am working on a wiring plan which includes a number of modine heat pumps with aux heat (EFV036). Heat pumps are spec'd at 208 3ph, 18 FLA, 21A MCA, 30 MOP
Aux 10kW heater is 208 1ph, 34.6 FLA, 34.6 MCA, 45 MOP.
I haven't seen these units yet, and the information I have found isn't real helpful. Do these units typically have two breakers built into the control box, and you run one branch circuit? Or do you have to run two branch circuits normally? Is there an option to add a small 2 breaker box on the unit, and a single branch circuit? If you can combine the loads, how do you calculate the branch MCA and MOP?
:?
Thanks,
Bryan
Aux 10kW heater is 208 1ph, 34.6 FLA, 34.6 MCA, 45 MOP.
I haven't seen these units yet, and the information I have found isn't real helpful. Do these units typically have two breakers built into the control box, and you run one branch circuit? Or do you have to run two branch circuits normally? Is there an option to add a small 2 breaker box on the unit, and a single branch circuit? If you can combine the loads, how do you calculate the branch MCA and MOP?
:?