Commercial HVAC equipment grounding

Status
Not open for further replies.
Dennis Alwon said:
Gotcha. I thought you were saying that the #10 was compliant with 250.122(B). Yeah, that was my point that the inspector missed the upsize. Instead of leaving the #8 with green tape--such a terrible thing :roll:-- he is calling for a #10 that is green-- a violation supposedly worse than what's there.

Now we are back on the same page:grin:
 
celtic said:
What if....
This circuit had been run using some flavor of AC cable..say a 6/3.
Would the cable now need to be removed and a similar flavor of MC installed?

The EI is out of touch here.

I guess you can't up size when using such cable....

All this ,....over a tape violation ,.... I'm gonna guess this guy is about 5'4":D
 