Commercial Kitchen EPO Station
AHE Tom
In what code section does it state the an EPO station is required in a commercial kitchen
I remember working on commercial kitchens in the past (10 years ago) and they all had EPO station to disconnect the kitchen equipment power
Thanks
Tom
I believe what you are talking about is a ANSUL system for a Commercial Kitchen hood.
The International Fire Code section 904.11.1 requires a manual actuation device located near a means of egress from the cooking area a minimum of 10 feet and a maximum of 20 feet from the kitchen exhaust system. This actuation device will actuate the fire suppression system and de-energize any electrical equipment located under the kitchen hood.
Chris
These EPO buttons were not for fire system, but shut down power to the panel serving the kitchen equipment
904.11.2 of the International Fire Code requires the actuation of the fire extinguishing system to automatically shut down the fuel or electrical power supply to the cooking equipment.
So what I usually see is an ANSUL button close to the door leaving a commercial kitchen that activates the fire suppression system and also disconnects the power to the kitchen equipment.
I am not aware of any code requirement for just a EPO button to shut down the power to the kitchen equipment without also initiating the fire suppression system.
Chris
Chris
What Chris said. We do about one kitchen suppression system every 2 weeks or so, and I have never heard of a separate EPO being required in a commercial kitchen. Maybe this is a spec thing that the owner requires? Local amendment? AHJ's whim?