Commercial Kitchens

Status
Not open for further replies.

jmd445

Senior Member
I have a freezer tripping a GFCI in a commercial kitchen. Does this appliance need to be on a gfci receptacle? I was going to change the receptacle to a single round 115v/20a but 210.8 (B)(2) states that ALL receptacles must be GFCI, there are no exceptions for a dedicated receptacle. Any ideas?

Jim
 
Yes I have a couple of ideas, the owner is not going to like either.

1) Relocate the refrigerator out of the kitchen.

2) Get a refrigerator that can operate on a GFCI.

There are no exceptions for commercial kitchen GFCIs.
 
I agree with Bob, there are no exceptions , commercial kitchen , all receptacles G.F.C.I.

Why do these appliances in commercial settings trip G.F.C.I's more often ,.... or does it just seem that way??
 
M. D. said:
Why do these appliances in commercial settings trip G.F.C.I's more often ,.... or does it just seem that way??


Perhaps because the equipment tends to be older and less maintained then a typical residential refrigerator/freezer. I have seen some ancient stuff in fairly upscale restaurants.

The newer equipment should not and will not trip a Class A gfci device if it is operating properly and within its listing.
 
bphgravity said:
Perhaps because the equipment tends to be older and less maintained then a typical residential refrigerator/freezer. I have seen some ancient stuff in fairly upscale restaurants.

No doubt.

There is a large trade in used restaurant equipment.

I have seen some real junk moved into brand new kitchens.
 
That's correct, this is an older refeer that was relocated. Probably a little break down in the compressor windings, condensate dripping on the evap fan motors, and the GFCI trips.

Jim
 
jmd445 said:
Probably a little break down in the compressor windings, condensate dripping on the evap fan motors, and the GFCI trips.

Add to that list the anitsweat heaters usually in the door and frame of commercial freezers.

If I was to try and see if it was an easy repair I would check the heaters for ground faults with a meter.
 