G Gaffen99 Senior Member Location new jersey Mar 15, 2009 #1 Is there any requirement for GFCI protection on 240 volt, 208 volt appliance outlets in a commercial kitchen? 210.8 only requires 125 volt.
Is there any requirement for GFCI protection on 240 volt, 208 volt appliance outlets in a commercial kitchen? 210.8 only requires 125 volt.
Pierre C Belarge Senior Member Location Westchester County, New York Mar 15, 2009 #4 480sparky said: No. Click to expand... Such a quick answer...lets think about this before we make such a fast decision. Me, I say NO. See 210.8(B) All 125-volt, single phase, 15-and 20-ampere receptacles installed in the locations specified in (1) through (5)... (2) Commercial and institutional kitchens -
480sparky said: No. Click to expand... Such a quick answer...lets think about this before we make such a fast decision. Me, I say NO. See 210.8(B) All 125-volt, single phase, 15-and 20-ampere receptacles installed in the locations specified in (1) through (5)... (2) Commercial and institutional kitchens -
G Gaffen99 Senior Member Location new jersey Mar 15, 2009 #5 Thanks, just wasn't sure if there was something buried somewhere in the latter of the book.