Use of nm cable in commercial building
Use of nm cable in commercial building
First and foremost, keep in mind this is outdated information ...
Years ago, I ran into a commercial rewire and found that NM (romex) was actually being specified. I conferred with the AHJ and then validated the info in the actual NEC at that time.
The two main factors were that it was only a two-story building and the COMMERCIAL USE was most critical -
If it was to be a gathering place where (I believe the specified limit was) 40 people or more would be expected, romex was not allowed ...
But in my case, it was being converted into a few offices with a staff that would be well under the 40 persons limit of a general meeting place ... romex WAS ALLOWED.
I would pay further attention to Infinity's reply:
"If the building is 10 years old than NM cable was likely permitted when the building was originally constructed. NM cable was allowed in structures not exceeding 3 stories above grade up to the 1999 NEC. In the 2002 NEC the prohibition changed to structures of certain construction types and the above hung ceilings prohibition was added as well.
So now under the 2005 NEC you would be permitted to use NM cable if it weren't above a hung ceiling and the building is of a construction type listed in 334.10."
It so happens I am beginning to research an related issue and came across your post. I feel like a dummy for not knowing the answer to my own question ... I have a 3-story building (with a penthouse added) that is a residential 4-plex. The first floor is being renovated (Hurricane Katrina) and MC cable was used throughout with one exception - the electrician used romex to some 120-vac lightin fixtures in cabinetry. The lights look like low-voltage surface mount cabinet/accents lighting, but the absence of a transformer is obvious. The surface mount fixtures are not suitable as junctions box for mc cable and retrofitting will be an expensive nightmare (wall are decorative tile ...).
Though the building may be considered more than three stories with the penthouse, am I still allowed to use romex as it is multi-family, combustible construction?