Thanks again for your reply. As you already know, 300.13(b) refers to multiwire branch circuits. The situation I'm concerned with here simply has two 12-2 mc's in a j-box to connect to a receptacle. One mc is bringing power in, and the other mc is continuing on to the next j-box/receptacle down the row - "snow chaining"
if you will. This isn't a multiwire branch circuit per the NEC definition because there is no voltage between the ungrounded conductors (they are the same circuit). If the neutral (grounded conductor) opens, no unbalanced voltage will occur in the downstream line-to-neutral loads as the neutral (grounded conductor) is not shared with any other circuits. Therefore, in this case, it doesn't appear that the neutrals (grounded conductors) are required to be pigtailed.? It's done all the time in residential work (no pigtails w/single circuit), but I haven't run across it much in commercial work and was just wondering if it was actually a written code applying specifically to commercial/industrial locations. Cheers