I ran across a refridgerator the other day with a nameplate stating the unit needed to be protected from overcurrent at 15A maximum. The unit was plugged into a 20A duplex receptacle which was protected by a 20 circuit breaker. The unit is also thermally protected.
I know of no exceptions that allow a themally protected peice of equipment to be protected at anything other than what the nameplate says it has to be (in this case 15A).
We still use the 2005 NEC here in Connecticut but I have never heard of an exception to this since I've been an electrician (<2005 or 2008). Am I wrong to tell management they have a problem here? There are other outlets on the same circuit; so replacing all the outlets to 15A as well as the breaker or running a new circuit is not producing any smiles (if you know what I mean). There are several of these installations throughout the facility so an exception would be very attractive to them.
So, does anyone have any information that would brighten their day?
I know of no exceptions that allow a themally protected peice of equipment to be protected at anything other than what the nameplate says it has to be (in this case 15A).
We still use the 2005 NEC here in Connecticut but I have never heard of an exception to this since I've been an electrician (<2005 or 2008). Am I wrong to tell management they have a problem here? There are other outlets on the same circuit; so replacing all the outlets to 15A as well as the breaker or running a new circuit is not producing any smiles (if you know what I mean). There are several of these installations throughout the facility so an exception would be very attractive to them.
So, does anyone have any information that would brighten their day?