synchro
 - Chicago, IL
 - EE
I wonder if the refrigerator has some internal ground fault detection circuitry of its own that is falsely tripping due to an interaction with the grounded neutral detection circuit in the GFCI breaker or receptacle (which Jon mentioned in his post #9 above). It seems hard to believe that a small test signal of several kHz at the line input of the refrigerator would directly cause internal digital logic in its controller to malfunction. But such a test signal intentionally has common-mode content, which ground fault detection circuitry is designed to pick up with a high level of sensitivity. A filter which attenuates such signals (as it seems the manufacturer is suggesting) might prevent this from happening.Just had a customer call and say their commercial refrigerator was malfunctioning, shutting off, circuit board resetting. He called the manufacturer, and they asked if it was on a gfi circuit, which it is. They said he needed some sort of filter, because their product doesn’t like gfi’s.