A duplex connector and bond bushing are the two that come to mind right off. Honestly, I'd try my best to not bring more than one MC to each box. If I needed lots of conductors, such as at a 2 or 3-gang switch box, I'd use a single MC with more conductors or snake down a piece of Greenfield.Pierre C Belarge said:Marc
How would you bond the multiple MC cables in the box?
Would you use a bonding type connector...if they make such a thing?
mdshunk said:A duplex connector and bond bushing are the two that come to mind right off. Honestly, I'd try my best to not bring more than one MC to each box. If I needed lots of conductors, such as at a 2 or 3-gang switch box, I'd use a single MC with more conductors or snake down a piece of Greenfield.