I am designing a commercial ESS plan set, and I am somewhat confused by contradicting information on the topic of conductor sizing. Here is the general information that is important to my question:
- 2023 NEC
- ESS only & using the grid power to charge the ESS. (utility allows this type of connection)
- ESS with a capacity 286.72kWh connected to the PCS (storage inverter) with an output of 125kW AC (Nameplate current rating: 151A)
- 200A fusible AC disconnect in between the PCS and a gutterbox that will use a polaris block to intercept the service feeders in between the CT cabinet and main distribution panel
- Service is 3p/4w 277/480V 800A
- AC terminals are rated 75C
- NEC 706.30(A)(1) says that the circuit current shall be the rated current indicated on the ESS nameplate or system listing
- 706.30(B) says that output circuit conductors of the ESS connected to the wiring system serving the loads to be serviced by the system shall not be less than the greater of 706.30(A)(1) [151A] or the rating of the ESS OCPD [200A]
- This is somewhat contradicted by this newsletter post (https://www.mikeholt.com/newsletters.php?action=display&letterID=2756) which mentions article 705 for ESS conductor sizing, even though there is no mention of article 705 in 706.30, and I dont think it is applicable
- Do I need to refer to article 705 for ESS conductor sizing?
- If I can use 706.30, do I need to take adjustment factors (conduit fill and temp) or can I just use the rating at 75C from 310.16?
- With an OCPD of 200A, this would mean I could either use 3/0 without adjustment factors or 300kcmil with adjustment factors (0.96 Temp Correction & 0.8 Current Carrying Conductors) (Assumed neutral as a current carrying conductor)
- The wording of 706.30(B) makes it seem like I wouldnt need adjustment factors for the conductor size, but I might be missing something there.
- Is there any scenario where you would use the nameplate rating instead of the OCPD because the OCPD has to be sized according to 705.31 which is 125% of the currents calculated in 706.30(A) meaning that the OCPD will always be higher than the nameplate rating.