Hey Everyone,
I have a Commercial service that will have a cold sequenced 200A fused disco. The panel being called out on the drawings is an MLO. I believe the cold disco meets the requirements of 230.70. However, for some reason (which is usually the case for me), I feel that a service disco on the load side of the meter is required. I suppose this is because the cold disco is technically in the PoCo's world? All Equipment is in the same building. Disco/ meter are outside and the MLO is inside. I also feel that the bond should be moved to the load side of the meter should it be concluded the MLO become an MCB panel.

Cheers....
I have a Commercial service that will have a cold sequenced 200A fused disco. The panel being called out on the drawings is an MLO. I believe the cold disco meets the requirements of 230.70. However, for some reason (which is usually the case for me), I feel that a service disco on the load side of the meter is required. I suppose this is because the cold disco is technically in the PoCo's world? All Equipment is in the same building. Disco/ meter are outside and the MLO is inside. I also feel that the bond should be moved to the load side of the meter should it be concluded the MLO become an MCB panel.