I have an 800amp service coming into a building. Where do I look to size the feeder wire for commercial applications?
See NEC-2008 Table-310.16 and also voltage drop, derating and other factors to size your feeder.
I have an 800amp service coming into a building. Where do I look to size the feeder wire for commercial applications?
Currently there are no voltage drop requirements in the NEC for typical feeders or branch circuits.
bob,
In NEC has already given a voltage drop calculation example and voltage drop is regardless the type of cable or branch or sepcific place.
I should use the 75d column correct?
The NEC does not require us to consider voltage drop in our calculations for most circuits.
The NEC is not a design specification.
Ok, thanks for this but I suggested him for sizing and designing feeder, he should also consider voltage drop, derating and other factors. Was I wrong?
Also if I am paralleling runs is it just additive? So 500mcm is good for 430 amps, so parallel it would be good for 860 amps? I am also seeing that I should use a #2 ground?
Wrong column, back up to 75C
Two 500 coppers in separate raceways will get you 760 amps of capacity and is allowed with an 800 amp breaker but should never be loaded beyond 760 amps.
Two 600 coppers in separate raceways will get you 840 amps of capacity.
If you decided to run two sets of say 4/0 copper in two raceways (four 4/0 per phase total) then the 90 C column would be useful.
It is legal and common to use two sets of 500s copper for 800 amps. Even though the ampacity is only 760 amps section 240.4(B) allows us to use an 800 amp breaker.
However the calculated load must never exceed 760 amps. This means if a year from now someone wants to add load they are supposed to do a full load calculation to make sure the added load does not bring the total over 760.
So since I am bidding against a group of guys that probably won't check any of this out, I think I will go with the 500's to not price myself out of the job.
You are correct. You would need parallel 700 kcm alum. for a 800 amp service as long as the calculated load is not greater than 750 amps. If not you may need parallel 900kcm alum. depending on the calculated load.So I just talked to my supplier and they are suggesting I go with aluminum conductors for the feed. Some electrician there was trying to say that I could use parallel 500mcm aluminum to feed an 800amp section. The way I read 310.16 is I would need at least 700mcm aluminum to feed 800amps. Am I right or is the other idiot right?