I'm not sure about your city/state revisions to the NEC, but here in Phoenix, AZ, Romex is NOT allowed in commercial buildings. Whatch your strapping of AC cable, within 6" of a junction/connector and at least every other stud/joist (48" max between supports) there after. Use the all-in-one snap-in AC connectors, thery are must faster to install and the anti-short is built-in. If you are running alot of AC or you have limited experiance running it, invest in a rotary AC cable splitter splitter. It will save you time and lots of frustration not to mention saving you from excessive trouble-shooting later on.
Your 2x4 flouresent lighting fixtures (trouffers) must be mechanicaly connected to the grid via the sheet metal/bend out clip in the franes of the fixtures, or separate screw on clips provide (most of the time) in your fixture hardware or by use of (2) two screws per end of the fixture. Your city / state my require the use of one of these methods over the other (can't go wrong with screws, just not too long or you will screw thought the tombstones). The grid wires (siesmic wires) must be suported separately from the ceiling wire and cannot attach to the grid or be used to support anything other than the fixture itself. You must attach a minimum of (2) wires per fixture on opposite/ diagonal corners. This is a good time to consider your emergency lighting. At battery back-up / emergency balast can kill two birds with one stone and emergency fixture assemblies (Troffers, with whips, ballasts and lamps factory installed) do not cost much more than your standard 2x4's.
What is the square footage of the building? I'm in a small TI right now, only 40,000 Sqft.
Your 2x4 flouresent lighting fixtures (trouffers) must be mechanicaly connected to the grid via the sheet metal/bend out clip in the franes of the fixtures, or separate screw on clips provide (most of the time) in your fixture hardware or by use of (2) two screws per end of the fixture. Your city / state my require the use of one of these methods over the other (can't go wrong with screws, just not too long or you will screw thought the tombstones). The grid wires (siesmic wires) must be suported separately from the ceiling wire and cannot attach to the grid or be used to support anything other than the fixture itself. You must attach a minimum of (2) wires per fixture on opposite/ diagonal corners. This is a good time to consider your emergency lighting. At battery back-up / emergency balast can kill two birds with one stone and emergency fixture assemblies (Troffers, with whips, ballasts and lamps factory installed) do not cost much more than your standard 2x4's.
What is the square footage of the building? I'm in a small TI right now, only 40,000 Sqft.