- Location
- New Jersey
- Occupation
- Journeyman Electrician
IMHO, as long as it reaches a given temperature, turns off and then turns back on "x" amount of minutes later I'm guessing it would be considered non-continuous.
That pretty much sums it up. If you peruse the Article 100 definition it must run at maximum current continuously for 180 minutes. If somewhere in that time frame it cycles off or to a lower output even for a few seconds it does not meet the deification of continuous load.