Is there a requirement in either the electrical or building code that states we have to install a common panel for a two or three family building?
 
Is there a requirement in either the electrical or building code that states we have to install a common panel for a two or three family building?
generally you have a house panel for things that are shared and the electricity from the house panel is paid for by the landlord. I don't think this is a NEC requirement though.
 
generally you have a house panel for things that are shared and the electricity from the house panel is paid for by the landlord. I don't think this is a NEC requirement though.
I don't either, local rules are when this typically is an issue.

Two family often there isn't any "house loads" to deal with. Over two family that possibility does often increase though.
 
See 210.25
Doesn't automatically mean you need a separate panel for "house" loads, only if there are "house" loads must they comply with that section.

Like I said often a two family dwelling doesn't have such loads, go to more dwellings and that chance of having such loads does increase.
 
Doesn't automatically mean you need a separate panel for "house" loads, only if there are "house" loads must they comply with that section.
So what you're saying is that there is an NEC requirement for "house" loads to be supplied from equipment other than the equipment which supplies an individual dwelling unit or tenant space.
 
Unless management pays for power, the concern is that a tenant could leave or lose power and the common areas would become deenergized.
 
Unless management pays for power, the concern is that a tenant could leave or lose power and the common areas would become deenergized.
What if owner stops paying utility bill or at least misses paying bill for whatever reason and the "house" gets disconnected? :unsure:

IMO this really should be design decision and not code. Probably still good design in most cases to have a separate house panel though.
 
So what you're saying is that there is an NEC requirement for "house" loads to be supplied from equipment other than the equipment which supplies an individual dwelling unit or tenant space.
Yes, but OP didn't give enough details so the answer to his original question is "maybe".
 
Is there a requirement in either the electrical or building code that states we have to install a common panel for a two or three family building?
It really depends on the "lay out" of the multifamily dwelling.
Most three family units that I have worked in do require a house meter.
You should check with the local building department.
As Kwired mentioned: Two family often there isn't any "house loads" to deal with. Over two family that possibility does often increase though.
 