Communication cable to gas island

Status
Not open for further replies.

storeytime

Member
Location
Texas
I'm installing 120V power for a card reader at a gasoline pump island. I'm not sure yet if the reader is wireless or hard wired. I'm waiting on the specs. If it is hard wired, will the conduit, conduit bodies, etc. fall under the same category as the requirements for the 120V power conduits to that area? It will be within about 5' of the pump, but not a part of the pump.
 
Last edited by a moderator:

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
If it's as close to the pump as you mentioned, the installation will fall under Article 514 whether it goes to the pump or not.
 