Communication systems & strikes
m sleem
Exemplary Сasual Dating - Genuine Females
Usa
Health
I have seen drawings showing a transient connection on ground between rods of communication system and rods of lightning ps, i know it's not required by code but the designer justified his design to disallow the return of lightning discharge, i said that we use the spd devices in all emergency panels per code including the communication, his justification which makes sense that grounding busbar in communication rooms are bonded together and go to ground, the equipment in communication room are bonded to busbar and go to rods belong to communication system accordingly there is no spd to disconnect the connection during strike unless we have a transient connection connected on ground,
If he is right, why nec doesn't require?
ceb58
Raeford, NC
That is a design issue. The NEC is not a design manual. You can find more detailed information from Motorola's R56 grounding guide lines.
m sleem
Usa
Health
IMHO, it's not a design issue, the NEC requirements shall provide a complete protection for building occupancies and equipment and even structure, but in this case the body of communication equipment is not fully protected during lightning strike.
ceb58
Raeford, NC
In what the OP describes is a standard grounding set up for a communication tower. Every thing is bonded together to keep every thing at the same potential in the event of a strike. You can have all the SPD on the panels you want but you want nothing to break the bonding connections. All equipment, panels, racks, fence and tower legs are all bonded together with one grounding system. We always joked at our tower sites that if you stood still for 5 min. someone would come by and connect a bond wire to you.
m sleem
Usa
Health
So, how you protect equipment bodies from damage due to the return path of lightning strikes?
tom baker
First Chief Moderator
Exactly correct on single point ground!
m sleem
Usa
Health
This is what i want to explain, the return of the strike would go to telecom equipments in case of bonded together,
Am i missing something?
CLDesigner
Columbus, Ohio
Technology grounding standard
The current grounding standard for technology is ANSI/TIA-607-C and is very detailed towards deign installation and testing requirements.
  • TIA-607 recommends a 6-awg bond between the power panel (providing power to the TR) ground bus and the Telecom Room (TR) busbar kit.
  • TIA-607 also recommends 6-awg bond to building steel but only where the building steel is not to be used as a lightning arrestor down-conductor. When building steel is used as a down conductor the recommendation is to provide separation (not attach).
  • There should be a separate telecom ground riser backbone that is bonded to building service entrance ground bus at only (1) point and otherwise isolated.
There are also NEC code references to incorporate.
  • 2017 NEC 800-53 requires 6' separation of communication cables to lightning arrestor down-conductors where practicable
  • NFPA 780 contains additional information on lightning arrestor system design.
jaggedben
Northern California
The lightning current has no particular desire to go to the server room. It might go there because it is inclined to go everywhere it can. It might, or might not, send much more current through the underground bonding wire than it would through the earth. After all, if that underground wire is bare copper as it should be, then the strike can discharge to the earth all along the route. To my understanding there isn't too much certainty about predicting exactly which way lightning will go.
One thing that strikes me as relatively certain though, is that if you don't bond the grounding systems with a 6awg wire at ground level, and the lightning finds some other unanticipated path through other wires above ground, it would do a lot more damage along that path than along a 6awg copper wire in the ground.
Finally, I believe the NEC requires the lightning system to be bonded to the premises grounding system so that in case the lightning system were to somehow be accidentally energized by a human-made source it would trip a breaker. Same principle as bonding water pipes and gas pipes. The imperatives of protecting people from human-made shocks and protecting against lightning damage do not dovetail well at all, to my understanding. Add to this a certain amount of grounding religion in some people's heads, and it may be quixotic to think all of the various codes and standards will make any kind of unifying sense.
tom baker
Again, Motorola R56 is the standard for telecom and cell towers. The cell companies use a single point ground....lightning wants to go to a earth ground, path to the equipment is high impedance.
m sleem
Usa
Health
Equipment's body is metal, how earth has lower impedance?
tom baker
I was a little to hasty on my last post. With a single point ground, there should be no difference in potential between the earth and equipment. No difference of potential, no current flow. The way I understand this, the lightning strike will elevate the local voltage somewhat, but since the electrical is all bonded together then no damage
The SPDs, serve to reduce transients that are induced on any power and communications/coax lines into the building