Communications and DC wiring for Photovotaic system

Status
Not open for further replies.

aelectricalman

Senior Member
Location
KY
I'm trying to find if my communications wiring and my DC wiring will both be permissable in the same raceway? The comm wire is part of the DC system! Also, I have reviewed 690.4 paragraph B, which states comm wire can not be run in the same raceway with AC branch circuits or feeder? Anyone have an opinion or fact? Does it fall under "same insulation type" requirement? Thanks again.
 

OTT2

Senior Member
Location
Orygun
When I look at 690.4(B) it looks to me that the separation is required for non-PV related wiring.

So this leads me to ask what type of conductor or cable is this "communications wiring"?

Do the installation instructions with this system address the installation you're proposing?
 