jap

Senior Member
Occupation
Electrician
Does compact aluminum conductors carry the same amperage as standard aluminum conductors?

also,

What table is used to determine conduit fill when using aluminum compact conductors?



JAP>
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes T310.15(B)(16) does not distinguish between compact and standard strand conductors. Conduit fill table are in Annex C. The tables with the (A) at the end are for compact strand.
 

sameguy

Senior Member
Location
New York
Occupation
Master Elec./JW retired
Years ago when they changed to the new aluminum mix and stranding the sales rep for Alcan, who lived across the street from me, showed me factory information compared to the old style.
It had better anti corrosion and better current capabilities.
Like said above you must follow the code amperage.
 