I agree that what it gets called is easily open to interpretation. But as far as the building steel to CCE or a ground ring is concerned that as well is considered a bonding jumper. Please correct me if I am misunderstanding this section.As far as the first 5 feet of water pipe being a grounding electrode vs the GEC or something else - IDK, but how does it compare to building steel or rebar making up a CEE that is extended outside the concrete? The building steel is not the true electrode, the portion that connects to earth is, and similar with rebar stubbed out of the footing for the purpose of connection to the GEC.
In most cases it kind of doesn't matter much as you can make bonding jumpers to other electrodes from either the GEC itself or from another electrode. The first 5 feet of water pipe can have a bonding jumper landed on it to another electrode, but it maybe isn't clear if it is truly the electrode or some kind of extension of the GEC which generally isn't allowed without irreversible connection means) which makes me lean toward the electrode extends up to 5 feet into the structure point of view.
How about a ground rod that has the GEC attachment above grade, but still has at least 8 feet of rod in the ground? That portion between the clamp and grade level part of the electrode or part of the GEC?
250.68(c)(2)