I have a multi-unit residential project (4 units).
All gas WH and cooking, but 2 units have electric clothes dryers, and 2 units have hot tubs.
Fridge, microwave, DW, furnace in all units.
Just for major appliances, not counting lighting load ( all LED, pretty minimal) and SABC (these are VRBO units, so owner supplies a coffee maker and that's it), I'm coming up with around 60kW GenSet.
Split service drop, so 2, 400A ATS will be required.
If I eliminate the hot tubs, that would help a huge deal. AHJ does not require us to do a full Article 220 load calc, (at least not on basic residential, they may on this one), I could probably get away with a 32kW, or at least a 38, with 200A ATS.
The Generac power management systems, well, I haven't heard much good about them.
So I was considering coming off the load side of the main breaker, installing a small box with a 15A breaker, and running a control wire to a 50A NC contactor in line with the hot tub feeder. Take the hot tubs off-line when utility power goes down.
Am I overlooking an easier solution?
All gas WH and cooking, but 2 units have electric clothes dryers, and 2 units have hot tubs.
Fridge, microwave, DW, furnace in all units.
Just for major appliances, not counting lighting load ( all LED, pretty minimal) and SABC (these are VRBO units, so owner supplies a coffee maker and that's it), I'm coming up with around 60kW GenSet.
Split service drop, so 2, 400A ATS will be required.
If I eliminate the hot tubs, that would help a huge deal. AHJ does not require us to do a full Article 220 load calc, (at least not on basic residential, they may on this one), I could probably get away with a 32kW, or at least a 38, with 200A ATS.
The Generac power management systems, well, I haven't heard much good about them.
So I was considering coming off the load side of the main breaker, installing a small box with a 15A breaker, and running a control wire to a 50A NC contactor in line with the hot tub feeder. Take the hot tubs off-line when utility power goes down.
Am I overlooking an easier solution?