HI everyone, I had a post yesterday regarding a 50HP compressor. Per NEC the FLA on a 50HP is 143 FLA. I originally had this on a 200amp breaker but revised it to a 250A breaker for starting purposes, I also am specifying a soft motor starter. My question, does everyone agree the 250A breaker will be ok for the compressor given I dont have any manufactuers data.
Secondly, my load calculation, (not shown in attached picture), is 299.5 amps, and that is taking 125% of the compressor into account. I have a 400A MCB in this panel, with all this equipment, do you guys think I should be going to a 600A MCB? My worry is that the compressor will fire up, along with some other piece of equipment, and it will blow the MCB in the panel.
Need opinions!
thanks
Secondly, my load calculation, (not shown in attached picture), is 299.5 amps, and that is taking 125% of the compressor into account. I have a 400A MCB in this panel, with all this equipment, do you guys think I should be going to a 600A MCB? My worry is that the compressor will fire up, along with some other piece of equipment, and it will blow the MCB in the panel.
Need opinions!