Since this condition only occurs during testing when both utility and Generator power is on, why can't you just shut down the compressors. During a normal utility outage this wouldn't be an issue. I don't see how using a closed transition would be effective unless a pending power loss was anticipated and the generators were spun up in advance.
Just out of curiosity, what kind of compressor Motors are we talking about? These aren't maglev Motors or anything like that are they?
Closed transition only operates an a hot bus - hot bus transfer, i.e. during a test from the controller touchpad or during retransfer to normal after a power outage. A CT transfer switch would definitely solve the problem since the transfer sine-wave is seamless but would be much more expensive on a 1200A switch than activating and wiring in the motor load disconnect with the existing ATS.