Compressor Wiring Solutions

Status
Not open for further replies.

chedore

GANEX
Location
Quebec, Canada
Occupation
Electromecanical technician, Automation Technician
Hello everyone. I need to change one of our compressors here in our shop and we were looking to buy a used 100HP compressor.
amprating100hp.png
On this image, we see that the Nameplate Amps of a 100HP compressor on 575V is 90.4A, and the Starter Amp rating would be 115A.

If I follow my intuition, we should load the wires/breaker to 80% of their capacity. Do I want to have higher capacity wires than breaker? Like if I use a 125A breaker, do I need to use 1/0 AWG wire?

Normally I'd go over to our electrician but this old fella is only here very early in the morning a few times a week and we need to make a decision.

Thanks for your time!
 
This probably should be moved to the canadian forum since the answer might be different than for US.

NEC answer:

Conductor ampacity is sized not less than 125% of the full load current found in the charts in the NEC, not the FLC found on the motor nameplate.

The circuit breaker can be sized up to 250% of the FLC found in the chart.
 