Does voltage ever drop enough the UPS takes over or at least beeps because it took over even if only for brief time?
Everything I am reading still says bad neutral or at least intermittently bad. What you don't know is if in your main panel, in your meter socket, at your service drop connection, or at some utility company connection anywhere between your service and the source transformer. If neighbor is on same transformer you both might be effected by same bad connection.
Best way to make this show itself is to load the system, but in an unbalanced fashion as in introduce high amount of 120 volt load to only one side of the 120/240 supply and then watch voltage as you load it.
If neighbor is on same transformer and the bad connection is in a common point ahead of both of you, his load balancing and your load balancing combine for an overall balance effect beyond whatever point is bad.
One other thing that maybe not too likely but not impossible - really long undersized utility conductors between utility transformer and your point of connection and/or undersized utility transformer for the load served. If you have several neighbors all on same transformer and it is undersized for the demand - you all will suffer voltage sags when loading is high but this will effect all loads not just line to neutral loads.
Voltage has never dropped for the UPS to take over, no beeps no nothing. The LEDs on the front report all good for voltage. Can I measure the voltage at an outlet when I load the system in an unbalanced fashion or do I need to do it at the main panel?