Loderunner
Member
should a computer floor grounding grid be attached to the building steel .
Yes, in addition every piece of conduit, pipe, raceway, floor pedestals, rebar it is near too. And that is just the end points. It should also be bonded to every SDS serving the area, all AC panel ground buses, and the GES. Then from the grid to every equipment cabinet in the area.Originally posted by Loderunner:
should a computer floor grounding grid be attached to the building steel .
Now Dereck I thought you were against multi-point grounding?By Dereck: Yes, in addition every piece of conduit, pipe, raceway, floor pedestals, rebar it is near too. And that is just the end points. It should also be bonded to every SDS serving the area, all AC panel ground buses, and the GES. Then from the grid to every equipment cabinet in the area.
Depends on the application. Single point isolated is only for special apps where manufactures require it. In most cases it is for telephone switching equipment made by Lucent, Nortel, etc.Originally posted by hurk27:
Now Dereck I thought you were against multi-point grounding?
Wouldn't it be better to single point everything back to the system grounding buss?
WoWBy Dereck What is stranger is Cisco use the grounding/bonding paths as a return for load currents along with return conductors. Have not quite figured out how they get it UL certified.