steveng said:i am providing 120volt receptacle circuits for 20 computers.
when calculating the load requirements for computers.
1. 3 computers per 20 amp circuit, sharing neutral?
each computer rated at 3.5 amp.
The potential of an overloaded neutral is only a problem with 3 phase wye systems.I know triplen harmonics from non-linear loads can overheat shared nuetrals on certain three-phase systems.
I can't find what type of system is susseptable to this problem.
I guess one could spend all sorts of resources on this, but generally speaking if they're standard work stations, I'll apply 500VA per station and get on w/ it. I tend to share (1) circuit w/ no more than (3) work stations as you've stated. Sometimes you'll need to pick up something else or end up w/ (1) station getting a dedicated circuit - it is what it is. I've never had any issue w/ the above method/philosophy.steveng said:i am providing 1 20volt receptacle circuits for 20 computers.
when calculating the load requirements for computers? should i use
1. 3 computers per 20 amp circuit, sharing neutral?
each computer rated at 3.5 amp.
danickstr said:computer load is a factor of the power supply which ranges from 250 watts to 600 or so. No need to overbuild your circuits if the systems are just small workstations with no real need for big graphics cards, which seem to be the main power hogs.