An oversized neutral on the MWBC's is also suggested and IMO preferable to dedicated circuits.charlie tuna said:ever heard of harmonics?? shared neutrals feeding computer equipment causes harmonic currents returning to the panel that do not cancel each other out like on normal loads. it's because the returning current is returning at a different frequency due to the switching in the computerized equipment's power supply. these harmonics are going to cause fluctuations in system voltages. every computer's instructions begin with the suggestion of installing it on a dedicated circuit.... if this common neutral was oversized enough the effects of harmonics would be lessened.
However, oversizing and/or dedicated neutral conductors do not alleviate harmonics on a system. With the exception of a minor change in voltage drop, all that changes under these different wiring methods is where the harmonics add up.
As I have learned here, the best [simple] solution is to put computer circuits on a single phase, three wire system. While there will still be switching distortion, at least it won't add up as on a three phase system.