I know of no prohibition. You need to maintain working clearances. If it is a large switchboard with a high current rating, the room will need a second exit. If you want to keep the room cool enough to protect the computers, the presence of the switchboard will force you to upsize the air conditioning equipment. It would not be my choice for room designs, but I think the NEC would allow it.
If the switchboard has exposed live parts, the story would be different. See 384-5 (1999 NEC) or 408.5 (2002 NEC).