ELA
Senior Member
- Occupation
- Electrical Test Engineer
I have a piece of equipment that has an IEC320 (computer type cable) with a female end plugged into the equipment. The other end of the cable has bare wires as opposed to having a nema 5-15 plug.
My question is can I use this cable which is #18/3 and rated to 10 amps, wire nutted into a 15 amp branch circuit?
I am guessing not but wanted to ask those who would know for sure.
I know that if the Nema 5-15 plug is used then it is considered plug connected equipment and the #18/3 wire is ok being plugged into a 15A branch circuit.
Since we are not using the plug but instead wire nutting the end in a junction box does this mandate a #14/3 cable?
Any way a tap rule can apply?
The cable is 6 ft long and SJT insulation. Load current is 3 amps maximum.
Thanks
My question is can I use this cable which is #18/3 and rated to 10 amps, wire nutted into a 15 amp branch circuit?
I am guessing not but wanted to ask those who would know for sure.
I know that if the Nema 5-15 plug is used then it is considered plug connected equipment and the #18/3 wire is ok being plugged into a 15A branch circuit.
Since we are not using the plug but instead wire nutting the end in a junction box does this mandate a #14/3 cable?
Any way a tap rule can apply?
The cable is 6 ft long and SJT insulation. Load current is 3 amps maximum.
Thanks