OK, here is what Mike Holt replied about using donuts and bonding around them:
Great Question! The best I can offer is:
250.96 Metal raceways, cable trays, cable armor, cable sheath, enclosures, frames, fittings, and other metal non-current-carrying parts that are to serve as grounding conductors, with or without the use of supplementary equipment grounding conductors, shall be effectively bonded where necessary to ensure electrical continuity and the capacity to conduct safely any fault current likely to be imposed on them.
Raceways, connectors and couplings are listed to have the capacity to conduct safely fault current. Reducing bushing are not listed, therefore they are not identified as having the capacity to conduct safely fault current.
God Bless, Mike Holt